Initial monitor settings

I just installed a new 500 A monitor for my two 100 Ah Lithium batteries (in parallel).

The batteries are activated, and appear to be fully charged (13.22 VDC each).

When I installed my monitor, it read 100% capacity, and the correct voltage, but only recognized 100 Ah.

Why doesn't it recognize my capacity as 200 Ah?

  • The monitors I am aware need to be setup including battery capacity. 100ah might be the default setting, Is it some sort of generic monitor or one from renogy that might have a manual?

  • I finally figured it out. I needed to set capacity in amp hours to 200 and then calibrate to 100%. It needed to be done in that order. I had reversed the two steps. It’s working correctly now. Thanks.